July 6, 2009

 

David,

 

I need help with this too.

 

 

254

Design Analysis

Provide year of applicable codes.

By FPE. – Will add to the Analysis.

255

Design Analysis

Reference to 13: 11.2.2.3.1 appears to be incorrect.

By FPE. – Typo – Should be 13:11.2.3.2.3.1.

256

Design Analysis

Verify use of schedule 10 pipe is acceptable based on corrosion testing or history. See 4-2.3.2 of UFC 3-600-01.

By FPE. – Will determine based on test results.

257

Design Analysis

Provide evidence of acceptance by NAVFAC FPE that no hose allowance is acceptable.

By FPE. – Verbal at this time.  Will obtain in writing.

 

 