July 6, 2009

 

David,

 

I need some help with these comments. Craig Seals is wanting me to finish this up today.

 

 

102

Dwg LS.1

Label wall ratings and show extent of the rated assembly. Show occupancies of all spaces. (Repeat Comment)

Miller – Will add to the LS Drawings.

103

Dwg LS.1

The Egress Capacity table should show “Required / Provided” to demonstrate Code compliance.

Miller – Will add to the LS Drawings.

104

Dwg LS.1

Briefing 203 needs 2 additional exits so that when the partition is positioned to make two separate rooms each room will have the required 2 exits.

Miller – We will verify the requirements.

105

Dwg LS.1

The door for RTUO 205 must be relocated so that it will not possibly be blocked by the door to room 213 Mech / Elec.

Miller – We will verify the requirements.

106

Dwg LS.2

Verify that the minimum width path of travel to exits has been provided and will remain unobstructed by trailer hitch tongues or any other portions of parked vehicles or equipment.

Miller – We will verify the requirements.

107

Dwg LS.2

Provide both “Required” and “Provided” in the Egress Capacity table.

Miller – Will add to the LS Drawings.

 

 